Is it necessary to have exterior lighting monitor and control to achieve this credit point. if interior is on BMS, Will i able to take that credit.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/17/2016 - 12:27

Both interior and exterior lighting must be automatically controlled. This is completed via BAS control, or via local automatic controls, including occupancy sensors and/or timers. 100% of site lighting and 100% of interior lighting for critical spaces, not exempted under ANSI/ASHRAE/IESNA Standard 90.1-2007, must have automatic controls in order to comply with the requirements of EAc3.1.