FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Automatic sliding doors in 90.1-2007 and LEED 3.0 Projects

I am working on project whereat a big retail store wants to use automatic sliding doors for their shop entrances. According to ASHRAE 90.1-2007, 5.4 Mandatory Provisions -> 5.4.3 Air Leakage -> 5.4.3.2 Fenestration and Doors, the air leakage shall not exceed 2.0 L/s*m² for that product. The manufacturer of the doors states that it is impossible to meet this requirment (they say a limit of 5.0 L/s*m² would be possible). ASHRAE 90.1-2007, p.18: "Air leakage shall not exceed 5.0 L/s'm2 for glazed swinging entrance doors and for revolving doors and 2.0 L/s·m2 for all other products." The automatic sliding doors will be used in vestibules. As I interpret it, the requirement is still 2 L/s*m², right? Has anyone used automatic sliding doors that meets the requirement? Or any other suggestions to solve that problem? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 05/04/2016 - 15:23

Will they be used for the inside or outside of the vestibule? If outside then I agree that the requirement you note applies. You might want to look at 90.1-2013 as there are more detailed requirements for additional fenestration/door types.