ASHRAE 90.1-2010 8.4.2 states, that 50% of all 125 volt 15- and 20-Ampere receptacle outlets in private offcies, open offices and computer classrooms shall be automatically switched off when the space is not occupied. In Germany, the power of receptacle outlets for "normal" devices such as computers, copiers or lighting is 230 volt 10 - 16 Ampere. Since it is not usual at all to switch off sockets or to have duplex receptacles with occupancy sensors or other controls it is very hard to implement this in german projects. The question is whether we have to follow the provision verbatim and apply this only to 125 volt outlets (which we do not have in Germany) or whether we should apply the requirement to our 230 volt outlets. We fear that many projects will choose a different certification system like DGNB or BREEAM in the last case. How do you work around this in other countrys? I´m interested in your opinion here. Thank you in advance! Best regards Jan
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
• The receptacle power density modeled for these spaces shall be the greater of 0.75 Watts per square foot (8.1 Watts per square meter) or the design coincident peak receptacle power density (if known).
• The receptacle schedule modeled in the Baseline for these spaces shall have a minimum Equivalent Full Load Hours of operation no less than:
o The ASHRAE 90.1-2010 User’s Manual default schedule for office occupancy (2,920 Equivalent Full Load Hours per year)
OR
o 120% of the occupied hours of operation for the facility
OR
o Detailed justification shall be provided supporting an alternate schedule.
• The Proposed model shall include either a 20% increase in the receptacle power density for these spaces OR a 20% increase in the scheduled receptacle Equivalent Full Load Hours of Operation versus the Baseline model. Our proposed project does not have Automatic Receptacle Control as per ASHRAE 90.1 2010 section 8.4.2. So I have followed the LEED Interpretation-ID# 10462 but I need some clarification as mentioned below.
- The receptacle power density modeled for these spaces shall be the greater of 0.75 Watts per square foot (8.1 Watts per square meter) or the design coincident peak receptacle power density (if known). – For Which Case we consider 0.75 Watts per square foot either BASE CASE or PROPOSED CASE?
- The Proposed model shall include either a 20% increase in the receptacle power density for these spaces OR a 20% increase in the scheduled receptacle Equivalent Full Load Hours of Operation versus the Baseline model. - The 20% increased receptacle power density whether consider from actual design or 0.75 Watts per square foot?