CI-2009 IEQc7.1:Thermal comfort - design

ASHRAE vs. ISO/EN

I am happy that LEED is accepting ISO 7730 and EN 15251 as alternative to ASHRAE 55. My problem is that there are no single requirements in these standards but examples / recommendations for design parameters for 3 different categories of comfort. In IEQp1 we are requested to meet the minimum requirements for ventilation. I would assume this is true for IEQc7.1 as well, and choose the least category. Does anyone have experience with submitting this credit following ISO / EN?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/31/2015 - 22:31

In v4, the EN and ISO standards are only for use on projects outside the US. I believe the same rule applies to the ACPs for v2009. That said, if you feel strongly about using something other than ASHRAE 55 for a project in the US, state your case to the reviewers. Your case should explain why the alternative is more appropriate, not that it might be simply easier.