Cooling system in our project (shopping mall) consists of dry-coolers sprayed with water. What are ASHRAE efficiency requirements for dry-coolers? Should they be qualified as air-cooled condensers in Table 6.8.1G?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5916 thumbs up
June 29, 2016 - 10:10 am
This sounds like an evaporative cooler which is covered in Table 6.8.1A.
Agnieszka Rylska
GO4IT SP Z OO SP K30 thumbs up
June 29, 2016 - 10:41 am
I just wanted to clarify that these dry-coolers are providing chill for heat pump units in tenant spaces. Cooling capacity of one dry-cooler is around 1500kW. I checked Table 6.8.1A and it seems that it covers smaller equipment. What do you think?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5916 thumbs up
June 29, 2016 - 11:13 am
I think I don't really understand what type of equipment you are trying to find. Can you pass along more specific information of the equipment? It is certainly possible that the type of equipment is not covered by any of the 6.8.1 tables. If that is the case there is no minimum efficiency you would need to meet. This happens frequently with equipment that is not commonly used in the USA.
Agnieszka Rylska
GO4IT SP Z OO SP K30 thumbs up
June 30, 2016 - 5:20 am
Dry-coolers are located on the roof of the building. Large fans create a forced airflow along heat exchangers. They are designed to provide cooling of Ethylene Glycol 35%. Additionally water is sprayed in the opposite direction to the air flow goiung through the coils in order to improve efficiency of the equipment. This system is then connected to the heat pump units which provide air conditioning in tenant spaces.
The equipment is similar to this: http://www.luve.it/cms/view/prodotti/co2-refrigeration-systems-special-o...
Agnieszka Rylska
GO4IT SP Z OO SP K30 thumbs up
July 1, 2016 - 10:06 am
Or should dry-coolers be qualified as cooling towers, do you have any thoughts on that? If not do you know who can I contact to confirm how this type of equipment should be qualified or to confirm that as you mentioned it's not covered by AHRAE?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5916 thumbs up
July 1, 2016 - 11:05 am
Thanks the details help. It is heat rejection equipment but this particular type is not covered under 90.1-2007. It was added to Table 6.8.1g in 90.1-2010. So technically it does not have a minimum efficiency requirement under LEED 2009.
Agnieszka Rylska
GO4IT SP Z OO SP K30 thumbs up
July 4, 2016 - 3:38 am
Thank you for your hepl!