CS-v4 EAp2:Minimum energy performance

ASHRAE Office Occupancy Schedule & Fan Control

Hi

I have a query regarding the ASHRAE Office Schedule. During normal occupancy hours the schedule is set to 95% occupancy, however our experience tells us that an 80% occupancy is typical for most offices. This can have an impact on fan consumption etc.

It is possible to use an alternative schedule that reflects a typical case per above?

Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/20/2019 - 16:12

There is no requirement to model ASHRAE default schedules. These are available if the actual schedules are unknown, but actual schedules are preferred for greater accuracy. 

Fri, 12/20/2019 - 22:13

Thanks Tyler. However in the case of Core & Shell, actual schedules are not known.  In this case, is it possible to use an alternative occupancy schedule to the ASHRAE default?

Sat, 12/21/2019 - 01:54

Yes, if you have a reasonable expectation that the alternative occupancy schedule is more accurate for the project than the ASHRAE default.  