FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

ASHRAE Mandatory Requirement 6.4.3.4.3

I have a multi-story building that has one AHU per floor taking OSA from a common vertical shaft. The OSA shaft is ducted, though does not have a fan to push the air in the building, and it is equipped with a gravity backdraft damper at the main intake. Each AHU though is not equipped with individual shut-off dampers at each floor. Thus when one AHU is off, the other AHU's that are operating cause the air to be siphoned backwards into the common OSA shaft. If my interpretation of the Mandatory Requirement is correct, each AHU should be equipped with a means of shutting the airflow from the common shaft when not operating. I have verified that reverse flow does happen on an identical building the owner has. I need to know if my interpretation is correct or does the main shut off damper meet the Mandatory Requirement. Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/28/2013 - 14:12

As long as the spaces served are all on the same schedule I think you meet 6.4.3.4.3. If the spaces/systems differ in their schedule then I think you would need dampers on each unit.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.