Requirements according to ASHRAE mandatory provision 5.4:
Cargo doors and loading dock doors shall be equipped with weather seals to restrict infiltration when vehicles are parked to doorway.
In our project there will be an open loading dock where several (two or more) trucks can dock at the same time and from the platform transport goods to the stores. During unloading the loading dock door (one) will be open.
Can we find compliance with another strategy, e.g. use double doors where one is always closed to prevent infiltration? Another method we considered is to use some kind of air curtains.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
September 11, 2012 - 9:37 am
I think that this mandatory provision only really applies to doors that a truck could back up to. If the facility has an outdoor loading dock then the trucks cannot be "parked in the doorway" and this provision would not apply.