FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Ashrae 90.1, section 6.4 minimun equipment efficiencies

Hello everyone We have a project in Uruguay in which our clients want to use a 350 tons centrifugal chiller with a 8.41 IPLV and 5.65 COP. Table 6.8.1C shows minimum efficiencies for this chiller are 6.40 IPLV and 6.10 COP. The proposed chiller does not meet the minimum COP requirements but exceeds by a lot the minimum IPLV requirements. Taking into account that the usual working point of a chiller is not at full power, could it be possible for this chiller to be accepted? Thank you. Agustin

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 05/23/2011 - 13:53

Technically equipment efficiency is a mandatory provision and the project must comply with both COP and IPLV. The efficiencies are determined at ARI test conditions. Check with the equipment manufacturer to make sure you are looking at the ARI efficiency values for your equipment.

Tue, 07/05/2011 - 09:39

When you say "The efficiencies are determined at ARI test conditions" does that mean the particular equipment has to be listed in the ARI certified database? Or is it adequate if the equipment is tested by the manufacturer under ARI conditions even though it is not listed under ARI database of certified products?

Thu, 08/11/2011 - 04:15

Augustine, I believe that this is a common problem in non- US projects. Ashrae 90.1 2007 refers to efficiencies determined at ARI conditions. I don't think it is necessary to be listed in ARI databse. However, the problem is not only ARI conditions. For your project in Uruguay, you will have a different set of leaving chiller water temperature and entering condenser temperature to Table 6.8.l (which are say 6.7 deg C and 29.4 deg C respectively). Even if you manage to get the the supplier to provide the COP and IPLV/NPLV under the ARI condtions at the required leaving chiller water temperature at 6.7 deg C and extering condenser water temperature of 29.4 deg C, it is likely the COP will not meet the minimum. However, page 32 of 90.1-2007 does state that these table values are only applicable over the following FULL LOAD design ranges: Leaving chiller: 4.4 to 8.9 deg C entering condenser: 23.9 to 29.4 deg C condener-water temperature rise: 2.8 to 8.3 deg C "Chillers designed to operate outide these ranges .........are not covered by this standard'' I would therefore believe that these equipments are not compliant to ashrae 90.1-2007, as outside the range does not default to compliance.

Wed, 10/26/2011 - 05:57

Dear guest experts, What are your views to my thoughts posted above? However, page 32 of 90.1-2007 does state that these table values are only applicable over the following FULL LOAD design ranges: Leaving chiller: 4.4 to 8.9 deg C entering condenser: 23.9 to 29.4 deg C condener-water temperature rise: 2.8 to 8.3 deg C "Chillers designed to operate outide these ranges .........are not covered by this standard'' I would therefore believe that these equipments are not compliant to ashrae 90.1-2007, as outside the range does not default to compliance Thanks

Wed, 10/26/2011 - 19:29

Equipment does not have to be in the ARI database, but you should be able to demonstrate performance at ARI conditions. I think we're largely arguing semantics here. If you've modeled the actual performance, and you are showing energy savings, my suspicion is that the LEED reviewers are pretty likely to accept it.

Mon, 11/14/2011 - 09:06

Christopher, You are saying that there is a chance that when HVAC equipment do not meet 90.1, or not covered in 90.1, can still meet LEED pre-requsite. IF the energy model proves the energy saving required. This is interesting. I thought pre-requsite refers to the prescriptve and mandatory items. This makes a huge difference.

Tue, 11/15/2011 - 14:32

Not exactly. You have to meet the mandatory items. You don't have to meet the prescriptive items if you are running an energy model. My point is, if you've got a piece of equipment that isn't listed, especially on a foreign project, but you can show that it has been modeled correctly and the model shows savings, I think the intent of the credit has been met.