In the CS- project the exit signs are considered to be a part of the emergency lighting. Therefore the lamps are off during normal operation. The proposed exit sign exceed 5 W per face. The exit sign needs 8 W, but only during operation. Could this case be considered an examption for the mandatory provisions ?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
June 26, 2012 - 12:34 pm
There are no listed exemptions to this mandatory provision.
Ralf Lehmann
M.Sc. | Dipl.-Ing. (FH) | LEED AP BD&CALPHA Energy & Environment GmbH
19 thumbs up
June 27, 2012 - 5:14 pm
Sorry, but we had the same experiance. I think you have to change. Maybe you take a look at Gessler. They have brilliant documentation. (I should carry to their account one day).
Martin Elezovic
Executive DirecorAtrium Consulting
June 28, 2012 - 5:55 pm
According to ASHRAE 90.1-2007 Section 9.1.1, Exception (a) (“emergency lighting that is automatically off during normal building operation”) it should be exempted from the Section 9 in general (Including mandatory provisions).
If some building feature is not in scope of the ASHRAE 90.1-2007 standard, is it still requested as mandatory requirement for LEED?
Eleni Thomidou
Bilfinger Baugesellschaft m.b.H.2 thumbs up
July 4, 2012 - 3:30 am
An answer to this last comment about exceptions would be very important and extremely interesting. Since in the project exit signs are part of emergency lights and according to local codes they are automatically off during normal building operation and automatically turned on in case of emergence, then we also assumed that it is exempted from Section 9. We are looking forward to hearing from you. Thank you in advance.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
July 26, 2012 - 11:55 am
I suppose if the local code says the exit signs are off during normal building operation then you could make the case for this blanket exemption.
In the US exit signs are required to be illuminated 24/7 so they are never exempt.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
July 26, 2012 - 12:20 pm
Martin,
If a building feature that impacts energy use is not covered by 90.1 it still must included in the energy models for LEED according to Appendix G and the prequisite/credit language. All energy use within and associated with the project must be included. So this is a requirement but not necessarily a mandatory provision as defined by 90.1. Even if you make the case that the exit signs are exempt from section 9 they must be included in the energy models.
Eleni Thomidou
Bilfinger Baugesellschaft m.b.H.2 thumbs up
July 26, 2012 - 2:07 pm
Hi! We have already submitted a CIR for this issue concerning the exemption from Section 9 Mandatory provisions, but your answer is definitely helpful and positive. Even if we are exempted we will include it in the energy model. Thank you very much!
Martin Elezovic
Executive DirecorAtrium Consulting
July 28, 2012 - 3:03 am
Marcus,
Thanks for clarifications. I also think it should be somehow included in energy simulation as requested by EAp2/c1. I would model it like this, in both proposed and baseline model:
- no lighting energy cost - exit sign lighting schedule is continuously off during the normal building operation; the only time when is on is during testing once per year or in case of electricity shortage and both cases can be neglected