Forum discussion

NC-2009 EAc1:Optimize energy performance

ASHRAE 90.1 appendix G - VAV modelisation in baseline system 7

Hi, I have a question about the interpretation of section G3.1.3.13 (VAV minimum flow setpoints). The G3.1.3.13 section states that the minimum volume setpoint for VAV reheat boxes shall be 2.15 l/s.m² (or 0.4 CFM/ft² in the IP edition). This minimum airflow concerns : - 100% outside fresh air - or could it include the minimum of outside air required by regulation with a recycling air complement? Many thanks by advance for your responses.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/12/2012 - 15:36

The full sentence is to use the value you mention or the minimum ventialtion rate, whichever is larger. Ventilation rate refers to the outside air, not included any recycled component.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.