NC-v4 EAp2:Minimum energy performance

ASHRAE 90.1-2010 Table 6.8.1c

Hello, 

There are two Paths in ASHRAE 90.1-2010 Table 6.8.1c water chilling packages -Efficiency Requirement, just would like to know what is the different between path A and path B?

Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 12/20/2021 - 21:52

It appears as if there is some explanation in Section 6.4.1.2.1. There might be more in the User's Manual.

Mon, 12/20/2021 - 22:01

The main difference is that Path A has slightly flatter kW/ton efficiencies for full load and part load, whereas Path B has criteria for a worse full load kW/ton but a much lower than Path A part load kW/ton efficiency.

Wed, 07/05/2023 - 01:35

Could you reload the link @Afogreen Build. tks u