We have a constant volume air fan feeding many floors. It feeds the mechanical space using it as a plenum. At the floor level there is a Supply fan serving the VAV and Fan boxes. The floor AHU only has a cooling coil, the heat is provided by reheats. Is it correct to use the maximum cfm for Vdzd and 100% for the Ds? When I use the minimum cfm for this calculation the required OA actually drops.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/11/2012 - 18:54

You will have to select the appropriate values for the worst case scenario for the floor level fan systems. In a typical VAV system, the worst case scenario is during heating mode, when system fan flows and zone air flows are both lower than 100% of design levels. However, you will have to experiment in the 62MZ calculator to determine which condition actually creates the highest requirement for outside air.