I have read that fire sprinkler systems are not addressed in LEED rating systems - does this also mean that a thread sealing paste used on the sprinkler piping does not need to comply to VOC limits for LEED?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Mara Baum
Partner, Architecture & SustainabilityDIALOG
674 thumbs up
August 13, 2012 - 6:32 pm
Tim, fire sprinkler systems are addressed in LEED, and products related to those systems inside the weatherproofing barrier and applied on site definitely need to comply with appropriate VOC requirements. Fire suppression systems are also addressed in EAc4.
Your sources are probably referencing credits MRc3-7. They require you to exclude fire sprinkler systems from the calculations -- in those credits sprinkler systems follow the same requirements as MEP equipment.