Forum discussion

NC-2009 EAc1:Optimize Energy Performance

Are exceptions mandatory or optional?

Under ASHRAE 90.1 - G3.1.1 do I HAVE to use exception C for any zones having special pressurization relationships, cross contamination requirements, or code-required minimum circulation rates? In my case this exception has a negative impact on my model. Can i stick with system 5? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 04/28/2015 - 15:43

You must apply the exceptions under G3.1.1.

Wed, 04/29/2015 - 13:14

Marcus, In an energy model for a LEED 2009 project it has been shown acceptable to model Baseline System Exceptions per ASHRAE 2010 G3.1.1 such as modeling a System type 9 or 10 for a heating only thermal zone. The exception in ASHRAE 2007 (G3.1.1 c) for using baseline single zone systems for zones that have code required minimum circulation rates was deleted in ASHRAE 2010 G3.1.1. Since this exception would no longer be allowed under a LEED Version 4 project, it would seem acceptable to follow ASHRAE 2010 and not model it in a LEED 2009 project. Is it acceptable to NOT model this exception (ASHRAE 2007 G3.1.1 c) since under ASHRAE 2010 it is no longer allowed?

Wed, 04/29/2015 - 13:23

Modeling a system 9 or 10 is allowed by addendum to 90.1-2007. If you can find an addendum to 90.1-2007 that eliminated exception c then you can use it. Keep in mind you must use it in its entirety. If it was not changed by addendum then you can't use it.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.