Forum discussion

NC-2009 IEQc4.2:Low-emitting materials - paints and coatings

Anti-corrosive system: VOC content of individual components

Dear all, The Contractor needs to install anti-corrosive paints / coatings for one project. The anti-corrosive system consists of 2 products (the first being an epoxy primer and the second being a polyurethane coating). I am assuming that, since this system is for anti-rust / anti-corrosion, both products have an upper VOC limit of 250g/L. Is this right, or should we consider the primer to have its own VOC limit (50 or 150g/L depending on whether it's flat or non-flat)? I feel that all the components of the anti-corrosive system must be treated under the same category with a maximum allowable VOC content of 250g/L. Any thoughts on that? Thanks..

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 02/27/2012 - 16:31

That's right - both products should independently meet the 250 g/L requirement.

Tue, 02/28/2012 - 09:34

Great, thanks Mara!

Wed, 03/05/2014 - 19:28

What if it is steel primer only? Then it would have to meet the 50/150?