Has anyone been successful using the alternative compliance path and submitting their own ASHRAE 62.1 calculation/spreadsheets in lieu of using the built in LEED or 62MZCalc form?
We would rather save time by not re-entering a ton of info and just provide a narrative and our calcs to prove we meet ASHRAE 62.1.
Dave Hubka
Practice Leader - SustainabilityEUA
LEEDuser Expert
495 thumbs up
October 31, 2015 - 9:32 am
While we have not submitted our own EQp1 calculations in lieu of the 62MZ we have been told by GBCI that non-62MZ calculations are acceptable.
As always, provide a detailed narrative explaining your methodology.
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
November 2, 2015 - 8:21 am
I think that it is unlikely that the LEED reviewer will accept your own spreadsheet. They provide a spreadsheet for you to use. I think it would take longer for you to convince them that you calculated multiple zones with unused OA correctly than it would to just fill out their spreadsheet. I recommend using the provided 62MZcalc.