I have some doubts concerning air loops of the baseline model, system 5 (Packaged VAV with Reheat).
Paragraph G3.1.3.13 “VAV Flow Minimum Flow Setpoints” states: “Minimum volume setpoints for VAV reheat boxes shall be 2.15 l/(s*m^2) of floor area served or the minimum ventilation rate, whichever is larger”.
How shall I calculate the “minimum air ventilation rate”? And the minimum outdoor air ventilation rate?
In the case that I’m modelling economizer is not requested because the climatic zone is 4a (see table G3.1.2.6A).
Must I model the baseline model with air recirculation?
Shall the air recirculation flow be equal to the total required supply air flow minus the minimum outdoor air ventilation rate?
With Regards