Forum discussion

NC-2009 IEQc5:Indoor Chemical and Pollutant Source Control

Air Recirc in DOAS/VRF Systems

This credit states to exhaust hazardous spaces with no air recirculation. I have a lab which is a single contained room with outside air and exhaust air ducted directly to the space from a dedicated outside air unit. The space is tempered by a VRF ceiling cassette unit which recircs the air within the space. Does this negate the intent of the credit as it relates to air recirculation?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/08/2012 - 19:55

The VRF unit would be doing local recirculation rather than recirculating the exhaust air from the space back into a full building system. The intent of the credit is to reduce the potentially contaminating other spaces. You may still be able to get the credit provided your meet the rest of the requirements. You could check for a LEED Interpretation or ask for one.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.