Mon, 05/03/2010 - 21:14

Hi JD and Brittany, the credit referenced standard is available from National Institute of Standardized Testing (NIST) by calling 800-553-6847 and follow the instruction as in Resources section of the LEED BD&C Reference Guide. More information on the publications is available at this website http://www.epa.gov/iaq/pubs/#I-BEAM In addition, we recommend using this standard available from the same sources: Compendium of Methods for the Determination of Toxic Organic Compounds in Ambient Air, Second Edition, Compendium Method TO-11A, Determination of Formaldehyde in Ambient Air Using Adsorbent Cartridge Followed by High Performance and Compendium of Methods for the Determination of Toxic Organic Compounds in Ambient Air, Second Edition, Compendium Method TO-17, Determination of Volatile Organic Compounds in Ambient Air Using Active Sampling Onto Sorbent Tubes, January 1999 Projects have successfully obtained the credit using this compliance path by following the testing procedures in these three resources. Some spaces that do not meet the testing criteria have to be retested again. A detailed report describing the testing procedures and results would be useful for the review team.