EBOM-2009 IEQp1:Minimum indoor air quality performance

AHU measurements

In our building we have two main AHU that supply 26 AHU (one for each floor of the building) and then we have VAVs for each zone in each floor. Do I need to perform measurements just in the two main AHU since this are the ones that have fresh air intake or we need to perform measurements in both the main and secondary AHU? Thank you in advance

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/11/2012 - 19:37

Luis, You will need to provide calculations/measurements for all the units. The calculations for the 26 units on each floor will dictate the OA requirements of the 2 main AHUs.