CS-v4 EAc3:Advanced energy metering

Advanced Energy Metering Owner & Tenant spaces

I have a G+6F C&S office building with 2 office spaces in each floor, which will be metered separately as per the local law. Although the owner of the building will be accommodating one of the largest office spaces in the building on the GF. My confusion is that, since they are the main owners and will be accommodating that space almost immediately after construction, will they need to follow the same requirements as the C&S? 

OR do we need to provide meters for any individual energy end use that represent 10% or more of the total annual consumption of the building specifically for the owner spaces?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 07/22/2022 - 15:17

The requirements for CS projects do not include the 10% of energy consumption requirement. The owner spaces are required to be metered in order to comply with the requirements of the prerequisite for Building-level energy metering. This credit is about the metering of tenant spaces.