FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Additional lighting power density in a retail store

Dear All, We are working on a shopping mall project which is pursuing LEED for C&S certification. According to table 9.6.1, maximum lighting power density for retail store is 18 W/sqm plus accent lighting. Since we don´t know which type of sales area is going to use the retail store, can we model the lighting power density considering "Sales Area Type 3" allowance according to table 9.6.2.? We would like to consider 44 W/sqm (Retail Sales Area 18 W/sqm + 26 W/sqm). Such lighting power density is close of what will be available for the tenants for interior lighting. Since there is not lighting design for tenant areas, we are going to use same allowance for baseline and proposed case. Best Regards.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 07/02/2015 - 07:43

We had C&S retail spaces without lighting design, where we included the highest additionial lighting power, since this was the worst case in our eyes. the reviewers were of the opinion, that in cases, where no retail lighting has been designed, only the 18 W/m² without any additionial lighting should be chosen. This was 1.5 years ago, since then we proceed in this way and never had a review comment on the 18 W/m².

Thu, 07/02/2015 - 12:46

Adding more LPD and modeling it identically is certainly the conservative approach. For this reason alone the reviewer should allow you to do so. The higher the neutral, identical energy use, the lower the overall savings.

Thu, 07/02/2015 - 21:05

Thank you very much Johannes and Marcus. Best Regards,