CS-v4 EAp2:Minimum energy performance

Acceptable Forms of a Tenant Lease Agreement | LEED Design Review Comments

Hi,

I am in the process of responding to a LEED reviewer comment concerning how to claim lighting power density reductions and improved HVAC efficiency in tenant spaces of a Core and Shell energy modeling submission.

For my initial LEED submission, I did provide the tenant lease agreement language which specified the minimum tenant HVAC efficiency requirements and the maximum tenant lighting power densities by space type. I was attempting to follow the direction given in LEED v4 manual on page 363 in the Core and Shell section: "projects can claim credit for energy reductions in tenant spaces if those reductions (such as lighting power density reductions or improved HVAC efficiency) are required through a tenant lease agreement or other legally binding document." I provided that information in my submission and therefore I claimed those tenant savings in my energy modeling.

However I received a LEED Design Review comment stating that an unsigned or sample lease agreement is not acceptable for claiming savings for the tenant spaces in the energy modeling. The LEED comment stated I needed to provide tenant lease agreements signed by both the building owner and tenants(s). In my case, I will need to provide multiple lease agreements as the project will have more than one building tenant. Finally, the comment said that cost savings cannot be claimed for any space for which there is not yet a tenant with a signed lease agreement.

The building owner right now is reluctant to provide the signed lease agreements because there being proprietary information within the agreements between the building owner and the various tenants. Unfortunately, given how the project is currently scoring overall, not taking credit for the tenant improvements could jeopardize whether the project becomes LEED certified.  

Differences in the LEED v4 manual and design review comment aside, my main question here is what is the best way to make everyone happy? Given the situation, my response to the LEED review comment is very important especially if I do not want to end up making further LEED appeals.

In my previous LEED Core and Shell design review experience (v2009), I understood that a signed letter of commitment from the building owner stating that a sample lease agreement (reviewed by LEED) used with future tenants was acceptable for claiming energy savings if the building was not fully occupied. The current LEED review comment I have states that is not the case anymore. Does anyone know if this requirement in fact has changed?

Any help or thoughts on this situation would be greatly apprenticed.

Thank you for your time in advance. 

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/23/2018 - 14:53

Yes this requirement changed. You could provide signed lease agreements with the proprietary parts redacted or maybe eliminated. The reviewer does not really need to see the whole agreement, just the parts that pertain to LEED and evidence that the agreement has been signed by both parties.

Thu, 08/23/2018 - 15:38

Thank you so much Marcus for your response. It was greatly appreciated, not "apprenticed". I missed that on the spell check. My mistake. :-)

Thu, 08/23/2018 - 17:12

Hi Eric, We have a whole lot of experience with this issue. Marcus is right. You only need to provide part of the documentation but it does need to include the following: page with project designation, page that indicates the exhibit that references the LEED requirements is part of the document, executed signatory pages, LEED exhibit pages. And all of these pages need to have the same footer on them.

Thu, 08/23/2018 - 17:35

Thank you for your help Michelle. I will be feeding this information back to the building owner.

Fri, 08/31/2018 - 19:19

Hi again, I got a follow up question today from the building owner and I was interested in getting everyone's take. The building owner has been investigating the tenant lease agreements and new challenges were identified in being able to produce the necessary documentation. So the building owner asked me today if a LEED reviewer would accept the actual tenant construction documents showing that the tenant spaces had been designed to meet the specified the minimum tenant HVAC efficiency requirements and the maximum tenant lighting power densities. Are tenant construction documents an acceptable alternative to seeing the tenant lease agreements for a LEED reviewer? For this project, the design firm I work for did the Core and Shell design. It also happens that my firm is currently designing 40% of the tenant space. So my firm in theory could provide the tenant construction documentation for that 40%.      Thoughts?

Fri, 08/31/2018 - 21:39

Maybe, but the drawings do not ensure that the tenant has leased the space. So some combination of drawings with evidence of a signed lease agreement instead of tenant requirements from the lease agreement might work.

Wed, 05/08/2019 - 12:49

Thanks Marcus, long story short this project's LEED certification is still being worked on and my response to the LEED reviewer’s comments have been delayed. Another question came up with the building owner recently and this goes back to my statement in August 2018 that the firm I work for did design some of the tenant spaces in addition to the main Core and Shell design. The tenant lease agreement specified minimum HVAC efficiency requirements. Now some of the tenant spaces my firm has worked on since the initial Core and Shell design submission had HVAC equipment with better efficiencies than what was outlined in the tenant lease agreement. The question was could my Core and Shell modeling within the tenant spaces my design firm worked on take credit for these better HVAC efficiencies over the tenant lease agreement?        

Wed, 05/08/2019 - 12:58

Yes if you now have final designs you can base those spaces on the final design instead of the lease agreement. Make sure you provide a complete narrative explanation to the reviewer.

Fri, 11/03/2023 - 21:22

Hi folks, is there a good resource somewhere with sample language for a lease agreement used for LEED certification purposes? 