Hello,
I work on my first PRM.
In the 9.4.1.2 mandatory provisions, the standart say:
"The controlled lighting shall have at least one control step between 30% and 70% (inclusive) of full lighting power in addition to all off." but we talk about manual control.
I don't understand if the baseline shall or not have automatic control.
Thanks for your help.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
August 4, 2016 - 11:11 am
See Table G3.1-6 Baseline. The Baseline shall have manual and automatic controls as indicated in Section 9.4. The specific item you mention can be accomplished with manual or automatic controls.
Ciaran McCabe
DirectorPassive Dynamics Sustainability Consultants
12 thumbs up
April 3, 2018 - 5:55 pm
Is it still applicable to use Table G3.2 in ASHRAE 2010 to represent Occupancy Sensors in the Baseline model (Automatic Controls).
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
April 4, 2018 - 9:31 am
Yes