NC-v4 EAp2:Minimum energy performance

90.1 2010: V4: Baseline Lighting Control

Hello, I work on my first PRM. In the 9.4.1.2 mandatory provisions, the standart say: "The controlled lighting shall have at least one control step between 30% and 70% (inclusive) of full lighting power in addition to all off." but we talk about manual control. I don't understand if the baseline shall or not have automatic control. Thanks for your help.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/04/2016 - 15:11

See Table G3.1-6 Baseline. The Baseline shall have manual and automatic controls as indicated in Section 9.4. The specific item you mention can be accomplished with manual or automatic controls.

Tue, 04/03/2018 - 21:55

Is it still applicable to use Table G3.2 in ASHRAE  2010 to represent Occupancy Sensors in the Baseline model (Automatic Controls).

Wed, 04/04/2018 - 13:31

Yes