We are working on a high rise multifamily building where the corridors are supplied with 100% semi-conditioned OA. This OA is used both for ventilation (62.1) and conditioning the space. Since this results in excess OA in the corridors than what is required by 62.1, the excess OA is also used as makeup air for the local exhaust in each apartment.

However, 90.1-2010 G3.1.2.6 Exception C, clearly states that any OA air in excess of the minimum for ventilation is penalized in term of energy (where as in 90.1-2007, this might not be the case).

I can understand the penalty for using OA to condition spaces, but shouldn't the baseline model be allowed to include OA as makeup for exhaust?

Thanks