How can we set the form to achieve the 5% of the total site area as described in the reference guide. Because in LEED online, it's the 25% path set as default.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »
Trista Brown
Project DirectorWSP USA
456 thumbs up
October 28, 2014 - 5:18 pm
Hi Maximiliano,
Unfortunately the form isn't able to accommodate this. I recommend creating an Excel spreadsheet showing the area required by the 25% path and the 5% path so that the reviewer can confirm that the 5% path is the greater of the two options (as the credit requires). Then I would also include a calculation showing that your native/adapted area meets the 5% path, since the form isn't able to show that.
And be sure to upload an excel version rather than a PDF so the reviewer can check out your work.
Hope this helps!