Forum discussion

CI-2009 IEQc1:Outdoor Air Delivery Monitoring

100% OA VAV Base Building system

Hi, the CI project I am working on uses only the base building system supply for meeting rooms with between 2 and 8 people. These rooms are all located internally and only use a temperature sensor to modulate the 100% OA VAV base building system. As the system is 100% OA there is ample ventilation being provided to the space. Also the VAV damper is connected to a temperature sensor that will modulate with the occupant density. I would like to confirm that our system meets the intent of the credit and that CO2 sensors are obsolete in this senario. Any meeting rooms with more than 8 people are provided with a supplementary system with temeprature and CO2 sensors.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 01/05/2016 - 17:31

There is no exception for a case like this, because there is still the potential that a VAV box could fully close or not open sufficiently, resulting in an indoor environmental issue. An issue could also develop at the air-handling unit itself where having carbon dioxide sensing would provide another layer of feedback. I do agree with the direction you're headed in conceptually, as this type of system has a greater chance of providing sufficient ventilation under all conditions versus a VAV system with a lower system level ventilation fraction.

Sun, 01/10/2016 - 22:08

Any system has the potential to not work resulting in an indoor environmental issue. The credit asks that a damper is connected to a CO2 sensor in the room. This has the same potential to not work as a VAV box. If there is a problem at the air-handling unit itself this would be picked up due to the temperature sensors as the rooms wouldn't be conditioned correctly.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.