Forum discussion

NC-2009 EAc1:Optimize energy performance

100% OA System vs baseline systems

I'm working on a model for a system designed for a small classroom building and have concerns on the proper baseline and proposed system ventilation rates. Thanks in advance for any advice or insight. The designed HVAC system is a VAV, 100% Outside Air Unit with an Relief/Outside Air Enthalpy Wheel with HW reheat. The unit includes a recirc damper to allow 100% return air during unoccupied periods, but does not provide for return air during normal operation or direct control of the outside air quantity at any time. The unit has a design airflow of 3,000 cfm and VAV minimum airflow of 800 cfm. My primary concerning is modeling the baseline ventilation rate. The building is non-residential,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/08/2013 - 21:13

Your thought seems to be correct (use ASHRAE 62.1 not IEQc2). The alternatives are incorrect. You only need DCV in the baseline if required by Section 6.4.3.9.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.