NC-2009 EAc3:Enhanced commissioning

10-Month Review

Does anyone have any advice on doing 10-Month Reviews? A past company I have worked at did a sample re-commissioning of the systems. The current company I am working with just wants me to take a short questionaire to the owner and general contractor to review performance. The LEED book isn't all that helpfull on this subject.

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/14/2011 - 17:42

The goal of the 10 month review is to identify any comfort problems as well as determine if there are any issues related to the efficient operation of the facility. This is best determined by a review of the comfort complaints from the occupants and an analysis of the building energy use. Depending on the findings of these efforts, additional work may be required and should be identified in an issues log. The log should define the issue, source of the problem (if known) and the party responsible for resolving the issue. The CxA is not necessarily responsible for resolving the issue unless that was part of their original contract.