I have a project attempting EAp2/c2 via the prescriptive pathway, Option 2, 50% AEDG. The only "required documentation" listed in the Reference Guide is the completed AEDG tables, which seems remarkably light. I don't want the team to be pummeled by review comments. I recall under v3 there was a LEED Online form for every section (envelope, hvac, lighting, etc.) and backup documentation to go with it.
What are other folks submitting in the way of documentation for the v4 prescriptive path? Any input is appreciated!
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
August 28, 2024 - 3:34 pm
Most of the time the best strategy is to provide only the information required. As reviewers we often see projects who provide too much contradicting themselves. If you think there might be a question about some of the input perhaps it would make sense to provide a narrative explanation.